For conductive pool shells, perimeter surface bonding must attach to the structural reinforcing steel or copper grid at a minimum of how many points?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10030
- C: 4 points uniformly spaced around the perimeter
Explanation
For conductive pool shells, perimeter bonding is attached to the reinforcing steel or copper grid at a minimum of four points uniformly spaced around the perimeter. For nonconductive shells the four point attachment is not required.