Question 10034 of 1033 · Washington 01 Journey Level Electrician Exam
Receptacles in an indoor spa or hot tub area must be located at least how far from the inside walls of the spa or hot tub?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10034
- D: 6 ft
Explanation
Receptacles at indoor spa and hot tub installations must be at least 6 ft measured horizontally from the inside walls. Receptacles within a larger distance must also be GFCI protected.