How must emergency system wiring generally be installed in relation to other wiring?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11004
- D: Kept entirely independent and not in the same raceway, cable, box, or cabinet as other wiring, with limited exceptions
Explanation
Emergency circuit wiring must be kept entirely independent of all other wiring and equipment. Exceptions cover transfer equipment enclosures, exit or emergency luminaires supplied from two sources, and certain common junction boxes.