Question 11023 of 844 · Washington 01 Journey Level Electrician Exam
May Class 2 conductors be installed in the same raceway as power conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11023
- A: No, except where separated by a barrier or as specifically permitted
Explanation
Class 2 and Class 3 conductors may not be placed in any cable, raceway, compartment, or enclosure with power conductors, unless permitted conditions such as barriers apply. This keeps power-level voltage off the low-energy wiring if insulation fails.