Under the NEC 2020 or 2023, what is the feeder load for 6 household electric dryers rated 6,000 W each?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12080
- D: 27,000 VA
Explanation
Each dryer counts at 6,000 VA (220.54): 6 x 6,000 = 36,000 VA. Six dryers take 75 %. 36,000 VA x 0.75 = 27,000 VA.