A 4,800 watt resistive water heater is connected to a 240 volt single-phase circuit. What is the current?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13002
- B: 20 A
Explanation
For a single-phase resistive load, I = P / E = 4,800 W / 240 V = 20 A. Using 120 V gives 40 A, and applying the three-phase factor 1.732 gives 11.5 A or 34.6 A, both wrong for a single-phase load.