A plant load of 100 kW operates at 0.80 power factor. About how much capacitor kVAR is needed to raise the power factor to 0.95?

Exactly one answer is correct.

Show solution

Correct answer to question 13023

  • C: 42.1 kVAR

Explanation

At 0.80 PF the reactive power is 100 x tan(acos 0.80) = 75.0 kVAR; at 0.95 PF it is 100 x tan(acos 0.95) = 32.9 kVAR. The capacitors must supply the difference, 75.0 minus 32.9 = 42.1 kVAR.