Question 13037 of 844 · Washington 01 Journey Level Electrician Exam

A three-phase 480 volt load of 100 A is 300 feet away. Ignoring ampacity, what is the smallest aluminum conductor that holds voltage drop to 3 %?

Exactly one answer is correct.

Show solution

Correct answer to question 13037

  • A: 1 AWG

Explanation

Allowed drop is 0.03 x 480 = 14.4 V, so CM = 1.732 x 21.2 x 100 x 300 / 14.4 = 76,499 circular mils, which requires 1 AWG (83,690). Using the copper K of 12.9 would wrongly point to 3 AWG.

Next to question ›