Question 13056 of 844 · Washington 01 Journey Level Electrician Exam

A raceway contains three 120/240 volt, single-phase 3-wire multiwire circuits. The neutrals carry only unbalanced current. What adjustment factor applies to the conductors?

Exactly one answer is correct.

Show solution

Correct answer to question 13056

  • D: 80 %

Explanation

The neutral of a 120/240 V 3-wire circuit carries only unbalanced current and is not counted, so there are 3 x 2 = 6 current-carrying conductors and 4 to 6 conductors require 80 %. Counting the neutrals as well (9 conductors) leads to the wrong 70 % factor.