A 4 inch by 1-1/2 inch square box (21.0 cu in) has a plaster ring marked 3.6 cu in. What is the maximum number of 12 AWG conductors permitted if nothing else is in the box?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13068
- D: 10
Explanation
Volumes of a marked ring or extension add to the box: 21.0 + 3.6 = 24.6 cu in, and 24.6 / 2.25 = 10.9, which rounds down to 10. The box alone allows only 9, and rounding up to 11 is not permitted.
More questions: Electrical Calculations
- 13069A box contains three 14 AWG insulated conductors that are spliced and terminated, two 14 AWG pigtails that originate and end inside the box, and one 14 AWG equipment grounding conductor group. What minimum volume is required?
- 13070Which volume allowance does 314.16(B) assign to each 6 AWG conductor?
- 13071A 4 inch by 1-1/2 inch octagonal box (15.5 cu in) will contain a fixture stud, four 14 AWG insulated conductors and one 14 AWG equipment grounding conductor. What volume is required, and does the box comply?
- 13072A 3 inch by 2 inch by 3-1/2 inch device box is rated 18.0 cu in. It holds a switch, two 14 AWG cables with grounds (4 insulated conductors) and internal clamps. How many additional 14 AWG insulated conductors may be added?
- 13073A conductor runs unbroken through a box without being spliced or terminated and is not looped. How is it counted for box fill?
- 13074What is the maximum fill percentage for a raceway that contains three or more conductors, other than a short nipple?