Question 13089 of 844 · Washington 01 Journey Level Electrician Exam
A 30 hp, 460 volt, three-phase motor has a table full-load current of 40 A. What is the maximum nontime-delay fuse size, using the next-higher-standard-size allowance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13089
- A: 125 A
Explanation
Nontime-delay fuses are limited to 300 %: 40 x 3 = 120 A. 120 A is not a standard size, so the next higher standard size of 125 A is permitted.
More questions: Electrical Calculations
- 13090What is the maximum setting, under the basic table percentage, of an instantaneous trip breaker for a 10 hp, 460 volt, three-phase squirrel-cage motor with a table full-load current of 14 A?
- 13091A motor has a nameplate full-load current of 24 A and a marked service factor of 1.15. What is the maximum rating of a separate overload device under 430.32(A)(1)?
- 13092A motor has a nameplate current of 40 A, a service factor of 1.0 and a temperature rise of 50 °C. What overload rating is required under the basic rule?
- 13093A motor with a 1.15 service factor and a nameplate current of 24 A trips its overloads during starting. What is the highest overload rating permitted under 430.32(C)?
- 13094A feeder supplies three 460 volt, three-phase motors with table full-load currents of 14 A, 21 A and 34 A. What is the minimum feeder conductor ampacity?
- 13095A 1 hp, 115 volt, single-phase motor has a table full-load current of 16 A. What minimum branch-circuit conductor ampacity is required?