Question 13110 of 844 · Washington 01 Journey Level Electrician Exam
A 40 A continuous load is supplied with THWN copper conductors terminating on 75 °C rated equipment. What is the minimum conductor size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13110
- B: 8 AWG
Explanation
The conductor must be rated for 40 x 1.25 = 50 A, and 8 AWG copper is rated 50 A in the 75 °C column. 10 AWG at 35 A fails, and sizing for 40 A without the 125 % factor might tempt someone to use the 90 °C rating of 10 AWG.
More questions: Electrical Calculations
- 13111A branch circuit supplies 30 A of continuous load and 20 A of noncontinuous load. What is the minimum standard overcurrent device rating?
- 13112What is the maximum continuous load permitted on a 20 A branch circuit protected by a standard (not 100 % rated) breaker?
- 13113What is the maximum continuous lighting load in volt-amperes on a 277 volt, 20 A branch circuit?
- 13114How many 277 volt LED luminaires drawing 0.75 A each may be connected to a 20 A branch circuit if they operate continuously?
- 13115A three-phase feeder supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum standard overcurrent device rating?
- 13116A 24 A continuous load is supplied by a branch circuit. What is the minimum overcurrent device rating and minimum copper conductor size with 60 °C terminations?