Question 2039 of 844 · Washington 01 Journey Level Electrician Exam
Service conductors installed under a building are considered outside the building when they are covered by at least how much concrete?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2039
- A: 2 in.
Explanation
Conductors installed under not less than 2 in. of concrete beneath a building, or in a raceway encased in at least 2 in. of concrete or brick within the building, are considered outside. Conductors under 18 in. of earth beneath a building also qualify. See 230.6.
More questions: Services and Service Equipment
- 2040How must each service disconnect be identified?
- 2041A detached building is supplied by one feeder. Where must its building disconnecting means be located?
- 2042Where may the service disconnecting means for a commercial building be installed?
- 2044A 480Y/277 volt switchboard faces a concrete wall (Condition 2). What is the minimum depth of the working space?
- 2045Overhead service conductors operating at more than 300 volts to ground pass over a residential driveway. What is the minimum vertical clearance?
- 2046Which edition of the NEC first required an outdoor emergency disconnect for one- and two-family dwelling services?