A series combination rating may not be used when motors connected between the two devices contribute more than what percentage of the lower-rated breaker's interrupting rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3004
- D: 1 percent
Explanation
Series ratings are not allowed where motors connected between the higher-rated OCPD and the lower-rated breaker have full-load currents totaling more than 1 percent of the interrupting rating of the lower-rated breaker. See 240.86(C).