Transformer secondary conductors not over 25 ft long must have an ampacity of at least what value?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3018
- D: One-third of the primary OCPD rating multiplied by the primary-to-secondary voltage ratio
Explanation
For secondary conductors up to 25 ft, the ampacity must be at least one-third of the primary OCPD rating times the primary-to-secondary voltage ratio. They must terminate in a single breaker or set of fuses. See 240.21(C)(6).
More questions: Feeders and Overcurrent Protection
- 3019What must the interrupting rating of a circuit breaker be at least equal to?
- 3020Why may an OCPD panelboard not be installed in a clothes closet?
- 3021What is the maximum OCPD rating for which the next size up rule may be used?
- 3022A feeder supplies 100 A of continuous load and 30 A of noncontinuous load. What is the minimum feeder conductor ampacity before any adjustment?
- 3023What is the role of a supplementary overcurrent protective device?