A 125-volt receptacle in an office break room is 4 ft from the break room sink. Is GFCI protection required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4024
- A: Yes, it is within 6 ft of the sink
Explanation
210.8(B) covers receptacles within 6 ft of the top inside edge of the bowl of a sink in other than dwelling units. The room does not need to qualify as a kitchen for this item to apply.
More questions: Branch Circuits, GFCI and AFCI