Question 4026 of 966 · Washington 01 Journey Level Electrician Exam
Under the 2020 NEC, a 50-ampere range receptacle in a dwelling kitchen is located more than 6 ft from the sink and does not serve the countertop. Is GFCI protection required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4026
- B: No, it is not covered by the 2020 kitchen or sink items
Explanation
In the 2020 NEC the kitchen item applied only to receptacles serving the countertop, and the sink item only within 6 ft. Electric ranges were not yet on a GFCI appliance list, so this receptacle was not required to be GFCI protected.