The required 20-ampere garage receptacle branch circuit in a dwelling is permitted to also supply which of the following?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4056
- C: Readily accessible outdoor receptacle outlets
Explanation
210.11(C)(4) states the garage circuit shall have no other outlets, but it may supply readily accessible outdoor receptacle outlets. Lighting and other rooms must be on other circuits.