Question 5036 of 844 · Washington 01 Journey Level Electrician Exam

What is the minimum copper equipment grounding conductor for a feeder protected by a 100 A OCPD?

Exactly one answer is correct.

Show solution

Correct answer to question 5036

  • D: 8 AWG

Explanation

Table 250.122 requires at least 8 AWG copper for OCPDs rated 100 A. The EGC is sized on the OCPD rating, not on the conductor ampacity.