Listed flexible metal conduit with listed fittings may serve as the EGC only where the circuit OCPD is rated not more than
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5043
- C: 20 A
Explanation
FMC may serve as the EGC if it is trade size 1 1/4 or smaller, the circuit is protected at 20 A or less, and the total length in the ground return path is 6 ft or less. See 250.118.