Question 6002 of 844 · Washington 01 Journey Level Electrician Exam

What is the minimum cover for rigid metal conduit or IMC under the general condition, 600 V or less?

Exactly one answer is correct.

Show solution

Correct answer to question 6002

  • B: 6 in

Explanation

RMC and IMC provide physical protection, so the minimum cover in the general location column is 6 in. See Table 300.5 in NEC 2020 and 2023; the underground installation rules are in 300.7 in NEC 2026.