Question 6022 of 844 · Washington 01 Journey Level Electrician Exam
Trade size 1 rigid PVC conduit must be supported at intervals not exceeding
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6022
- B: 3 ft
Explanation
Table 352.30 requires supports at 3 ft maximum for PVC trade sizes 1/2 through 1, with longer spacing allowed for larger sizes. PVC must also be fastened within 3 ft of each box or termination.
More questions: Wiring Methods, Conductors and Boxes
- 6023Expansion fittings are required in a run of PVC conduit where the expected length change due to temperature is at least
- 6024NM cable must be secured at intervals not exceeding
- 6025NM cable must be secured within what distance of every cable entry into an enclosure such as an outlet box?
- 6027Type MC cable must generally be secured within 12 in of each box and at intervals not exceeding
- 6028Type AC cable must be secured within 12 in of each box and at intervals not exceeding
- 6033In NEC 2020 and 2023, what is the maximum total of bends permitted in a run of EMT between pull points?