Question 7020 of 966 · Washington 01 Journey Level Electrician Exam
A snap switch is replaced in an old box that has no grounding means. Which installation is permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7020
- C: A noncombustible nonmetallic faceplate with nonmetallic screws, or GFCI protection
Explanation
An exception to 404.9(B) covers replacements where no grounding means exists. The switch then needs a nonmetallic, noncombustible faceplate with nonmetallic screws, or the circuit must be GFCI protected.