Correct answer to question 7035
- D: The identification and location of the source that supplies it
Explanation
Section 408.4(B) requires panelboards and switchboards supplied by a feeder in other than one- or two-family dwellings to be permanently marked with where the power supply originates. This helps workers find the correct disconnect quickly.