Question 7042 of 844 · Washington 01 Journey Level Electrician Exam
Which item is prohibited within 3 ft horizontally and 8 ft vertically of a bathtub rim?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7042
- A: A chain-suspended pendant luminaire
Explanation
Section 410.10(D) prohibits cord-connected luminaires, chain, cable or cord suspended luminaires, lighting track, pendants and ceiling-suspended paddle fans in that zone above a bathtub or shower. People standing in the tub could touch them.
More questions: Equipment, Devices and Luminaires
- 7043A luminaire in the bathtub zone is subject to shower spray. What must it be marked for?
- 7044A recessed luminaire that is not identified as Type IC is installed in an insulated ceiling. How far must thermal insulation be kept from the luminaire?
- 7045What does a Type IC marking on a recessed luminaire mean?
- 7046What is the maximum luminaire weight an outlet box may support unless the box is listed and marked for more?
- 7047Fluorescent luminaires with double-ended lamps and ballasts in a commercial building need what feature for servicing?
- 7048A fixed storage water heater holds 50 gallons. What is the minimum branch-circuit rating based on the nameplate?