What is the maximum rating of an inverse time breaker used as motor branch-circuit short-circuit and ground-fault protection for a standard squirrel cage motor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8011
- A: 250 percent of full-load current
Explanation
Table 430.52 sets inverse time breakers at a maximum of 250 percent of the table full-load current for single-phase and polyphase squirrel cage motors other than wound-rotor and dc motors. The high value allows the breaker to ride through starting current.
More questions: Motors, HVAC, Generators and Transformers
- 8012What is the maximum rating of a dual-element time-delay fuse used as motor branch-circuit short-circuit and ground-fault protection?
- 8013What is the maximum rating of a nontime delay fuse used for motor branch-circuit short-circuit and ground-fault protection?
- 8014What is the maximum setting of an instantaneous trip breaker for a squirrel cage motor other than Design B energy efficient?
- 8015The calculated motor short-circuit protection value does not match a standard size. What does 430.52 permit?
- 8016A three-phase motor has a table full-load current of 40 A. What is the maximum inverse time breaker rating for its branch circuit, without using exceptions?