Which nameplate value is used to size branch-circuit conductors for a packaged air conditioning unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8039
- B: Minimum circuit ampacity (MCA)
Explanation
Equipment with hermetic motor-compressors is marked with a minimum circuit ampacity under 440.4(B), and the conductors must be at least that value. The MCA already includes the 125 percent factor for the largest motor.