Question 8059 of 966 · Washington 01 Journey Level Electrician Exam
An optional standby system uses an automatic transfer switch and no load management. What capacity must the system have?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8059
- D: Enough to supply the full load that is transferred
Explanation
Optional standby systems with automatic transfer and no load management must be sized for the full load that can be transferred. This is 702.4(B)(2) in NEC 2020 and 702.4(A)(2) in NEC 2023 and 2026. An energy management system that automatically limits the load can reduce the required capacity, while with manual transfer the user chooses which loads to connect.
More questions: Motors, HVAC, Generators and Transformers
- 8060Under the 2020 and 2023 NEC, a permanently installed generator at a one- or two-family dwelling needs which additional device?
- 8061A transformer rated 1000 volts or less has primary protection only, and the primary current is 9 A or more. What is the maximum primary overcurrent device rating?
- 8062A small control transformer has a primary current of 5 A and primary protection only. What is the maximum primary overcurrent device rating?
- 8063A transformer with primary-only protection has a rated primary current below 2 A. What is the maximum primary overcurrent device rating?
- 8064A transformer rated 1000 volts or less has both primary and secondary protection. What is the maximum primary device rating?
- 8065With primary and secondary protection, what is the maximum secondary device rating for a transformer with a secondary current of 9 A or more?