Question 9015 of 966 · Washington 01 Journey Level Electrician Exam
Threaded rigid metal conduit in a Class I, Division 1 location must be made up wrenchtight with at least how many fully engaged threads?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9015
- A: Five
Explanation
Threaded joints in Class I, Division 1 must be made up wrenchtight with at least five full threads engaged. This helps the joint act as a flame path and keeps the raceway effective as an equipment grounding path.