Question 9022 of 844 · Washington 01 Journey Level Electrician Exam
The emergency electrical disconnect for fuel dispensers must open which conductors of the circuits to the dispensing equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9022
- C: All conductors including the grounded conductor, if present
Explanation
Circuits leading to or through dispensing equipment must have disconnects that open all conductors simultaneously, including the grounded conductor. This removes every source of voltage from the dispenser for servicing and in an emergency.
More questions: Special Occupancies
- 9026In a major repair garage for gasoline vehicles without the specified mechanical ventilation, how is the floor area up to 18 in above the floor classified?
- 9029In health care facilities, a patient care space where failure of equipment or the electrical system is likely to cause major injury or death is which category?
- 9030A patient care space in which failure of equipment is likely to cause only minor injury to patients or caregivers is classified as which category?
- 9031Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?
- 9035The essential electrical system of a hospital is divided into which branches?
- 9036Article 518 for assembly occupancies applies to buildings or portions of buildings designed for the gathering of how many persons or more?