Question 9027 of 966 · Washington 01 Journey Level Electrician Exam
The interior of a spray booth used for applying flammable paint is classified as which location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9027
- C: Class I, Division 1 or Zone 1
Explanation
Article 516 classifies the interior of spray booths and rooms where flammable materials are sprayed as Class I, Division 1 or Zone 1. Ventilation affects the extent of surrounding Division 2 areas, but not the classification of the booth interior.