Question 9037 of 1033 · Washington 01 Journey Level Electrician Exam
Which wiring method is generally permitted throughout an assembly occupancy under Article 518?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9037
- D: Type MC cable
Explanation
Assembly occupancies generally require metal raceways, nonmetallic raceways encased in concrete, Type MI, MC, or AC cable with an insulated EGC. Type NM is limited to cases where the building construction type permits it, and cord is not a substitute for fixed wiring.