Question 9049 of 1033 · Washington 01 Journey Level Electrician Exam
In an RV park, what minimum percentage of the sites with electrical supply must each have a 50-ampere, 125/250-volt receptacle?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9049
- B: 40 percent
Explanation
At least 40 percent of RV sites with electrical supply must have a 50-ampere, 125/250-volt receptacle, reflecting larger modern RVs. The 70 percent figure applies to 30-ampere receptacles.