Question 9060 of 966 · Washington 01 Journey Level Electrician Exam
On construction sites, a box is not required for splices or junctions in which of the following?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9060
- D: Multiconductor cord or cable assemblies, when using approved fittings or the circuit conductors of portable cords
Explanation
Temporary wiring rules allow splices in multiconductor cord or cable on construction sites without a box when the splice is made with approved methods. Permanent wiring methods such as concealed NM or raceway conductors still require boxes.