In NEC 2020 and 2023, fire pump supply conductors inside a building may be protected by encasement in at least how much concrete?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10077
- C: 2 in
Explanation
Fire pump supply conductors routed through a building must be protected from fire damage. One permitted method in NEC 2020 and 2023 is encasement in not less than 2 in of concrete.