A transformer arc welder has a rated primary current of 50 amperes and a 50 percent duty cycle. The I1eff value is not marked. Using a duty cycle multiplier of 0.71, what is the minimum supply conductor ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10083
- C: 35.5 amperes
Explanation
When I1eff is not given, the supply conductor ampacity is the rated primary current multiplied by the duty cycle factor: 50 A x 0.71 = 35.5 A. Applying a 125 percent factor here is a typical error.