A fire pump motor has a full-load current of 40 amperes and no accessory loads. What is the minimum ampacity of the supply conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10081
- A: 50 amperes
Explanation
Fire pump supply conductors must have an ampacity of not less than 125 percent of the motor FLC plus 100 percent of accessory loads: 40 A x 1.25 = 50 A. The OCPD is sized separately, based on locked-rotor current.