Question 1046 of 844 · Washington 01 Journey Level Electrician Exam
On a 208Y/120-volt three-phase, four-wire system, what voltage is measured from any phase conductor to the neutral?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1046
- B: 120 volts
Explanation
On a 208Y/120 system the line-to-neutral voltage is 120 V and the line-to-line voltage is 208 V, because 120 x 1.732 is about 208.
More questions: Definitions, Theory and Plans
- 1047On a 480Y/277-volt system, what is the voltage between any two phase conductors?
- 1048In a delta-connected transformer winding, the line current equals the phase (winding) current multiplied by:
- 1049On a 240/120-volt three-phase, four-wire delta system with a center-tapped winding, the high leg measures approximately how many volts to the neutral?
- 1050On a balanced three-phase, four-wire wye system serving only linear resistive loads, the neutral current is:
- 1051On a wye system serving many computers and LED drivers, which harmonics add together in the neutral instead of canceling?
- 1052Which expression gives the true power of a balanced three-phase load?