Question 1069 of 844 · Washington 01 Journey Level Electrician Exam
An insulation resistance tester (megohmmeter or megger) checks insulation by:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1069
- A: Applying a high DC test voltage and reading resistance in megohms
Explanation
A megohmmeter applies a high DC voltage, commonly 500 or 1,000 V, between conductors or to ground and displays the leakage resistance in megohms. It is used on de-energized equipment.