Under the NEC, operation of equipment in excess of its normal full-load rating that would cause damaging overheating if it persisted is called:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1093
- D: An overload
Explanation
Article 100 defines overload as operation in excess of normal full-load rating, or of a conductor in excess of its ampacity, that causes damage or overheating if it lasts long enough. A short circuit or ground fault is not an overload.