Question 12024 of 844 · Washington 01 Journey Level Electrician Exam

Under the NEC 2020/2023 standard method, what is the demand load for general lighting, two small-appliance circuits and one laundry circuit in a 4,500 ft2 dwelling?

Exactly one answer is correct.

Show solution

Correct answer to question 12024

  • D: 8,250 VA

Explanation

4,500 ft2 x 3 VA = 13,500 VA, plus 4,500 VA for the small-appliance and laundry circuits = 18,000 VA. First 3,000 VA at 100 % and the remaining 15,000 VA at 35 % gives 8,250 VA (Table 220.42 in 2020, Table 220.45 in 2023).

Next to question ›