A dwelling has one electric dryer rated 3,800 W. What load must be used for it in the NEC 2020/2023 service calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12032
- D: 5,000 VA
Explanation
Household dryers count at 5,000 VA or the nameplate rating, whichever is larger (220.54 and Table 220.54). Since 3,800 W is below the minimum, 5,000 VA is used, and one dryer takes a 100 % demand factor.