Under the NEC 2020 or 2023, which load is left out of a dwelling neutral calculation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12091
- C: A 240 V central AC unit
Explanation
Only line-to-neutral load contributes to the neutral (220.61). A 240 V air conditioner draws no neutral current, while ranges and dryers count at 70 %.
More questions: Load Calculations
- 12092Under the NEC 2020 or 2023, the optional method of 220.82 may be used for a single dwelling when the service or feeder is:
- 12093NEC 2020/2023 220.83(A): an existing 1,600 ft2 dwelling with two small-appliance and one laundry circuit, a 12 kW range, 5 kW dryer and 4.5 kW water heater gets no new heating or AC. What is the calculated load?
- 12094NEC 2020/2023 220.83(B): an existing 2,000 ft2 dwelling (two small-appliance and one laundry circuit, 11 kW range, 5.5 kW dryer) adds a 6,000 VA central AC. What is the calculated load?
- 12095Under NEC 2020/2023 220.83, what portion of the existing general load is counted at 100 % before the 40 % factor applies?
- 12098Which is a condition for using the NEC 2020/2023 multifamily optional method of 220.84?
- 12099An existing 200 A service shows a 1-year maximum demand of 110 A. A 40 A load is added. Using NEC 2020/2023 220.87, what is the resulting calculated load?