Which is a condition for using the NEC 2020/2023 multifamily optional method of 220.84?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12098
- B: Each unit has electric cooking
Explanation
220.84(A) requires that no unit be fed by more than one feeder, each unit have electric cooking equipment, and each unit have electric space heating, AC, or both.
More questions: Load Calculations
- 12099An existing 200 A service shows a 1-year maximum demand of 110 A. A 40 A load is added. Using NEC 2020/2023 220.87, what is the resulting calculated load?
- 12101Under NEC 2020/2023 220.60, a dwelling has 10 kW of electric heat and a 5,000 VA AC unit that do not run together. What load is used in the standard method?
- 12102An 8-unit building has 900 ft2 units, each with two small-appliance and one laundry circuit. What is the NEC 2020/2023 standard method demand for these loads?
- 12104A small store has 40 duplex receptacles. What receptacle load is used under the NEC 2020 or 2023?
- 12105A store has 45 ft of show window. What lighting load is required for the window under the NEC 2020 or 2023?
- 12106Under the NEC 2020 or 2023, a strip mall has three required sign outlets. What sign load is included?