Question 12102 of 844 · Washington 01 Journey Level Electrician Exam
An 8-unit building has 900 ft2 units, each with two small-appliance and one laundry circuit. What is the NEC 2020/2023 standard method demand for these loads?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12102
- B: 22,110 VA
Explanation
Each unit is 900 x 3 VA + 4,500 VA = 7,200 VA, for 57,600 VA in total. With the dwelling demand factors: 3,000 + 54,600 VA x 0.35 = 22,110 VA.
More questions: Load Calculations
- 12104A small store has 40 duplex receptacles. What receptacle load is used under the NEC 2020 or 2023?
- 12105A store has 45 ft of show window. What lighting load is required for the window under the NEC 2020 or 2023?
- 12106Under the NEC 2020 or 2023, a strip mall has three required sign outlets. What sign load is included?
- 12107What load is used for 60 ft of track lighting in a showroom under the NEC 2020 or 2023?
- 12108A 30 ft multioutlet assembly will have several appliances used at the same time. What load applies under the NEC 2020 or 2023?
- 12114Under the NEC 2020 or 2023, what load is calculated for each 2-wire laundry branch circuit in a dwelling?