A small store has 40 duplex receptacles. What receptacle load is used under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12104
- D: 7,200 VA
Explanation
40 x 180 VA = 7,200 VA (220.14(I)). Because the total is under 10 kVA, no demand factor reduces it.