An existing 200 A service shows a 1-year maximum demand of 110 A. A 40 A load is added. Using NEC 2020/2023 220.87, what is the resulting calculated load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12099
- C: 177.5 A
Explanation
220.87 takes the 1-year maximum demand at 125 % and adds the new load: 110 x 1.25 = 137.5 A, plus 40 A = 177.5 A, which the 200 A service can carry.