Question 12093 of 844 · Washington 01 Journey Level Electrician Exam
NEC 2020/2023 220.83(A): an existing 1,600 ft2 dwelling with two small-appliance and one laundry circuit, a 12 kW range, 5 kW dryer and 4.5 kW water heater gets no new heating or AC. What is the calculated load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12093
- A: 17,120 VA
Explanation
Total load = 4,800 lighting (3 VA/ft2) + 4,500 + 12,000 + 5,000 + 4,500 = 30,800 VA. 220.83(A) takes the first 8 kVA at 100 % and the rest at 40 %: 8,000 + 22,800 VA x 0.4 = 17,120 VA.
More questions: Load Calculations
- 12094NEC 2020/2023 220.83(B): an existing 2,000 ft2 dwelling (two small-appliance and one laundry circuit, 11 kW range, 5.5 kW dryer) adds a 6,000 VA central AC. What is the calculated load?
- 12095Under NEC 2020/2023 220.83, what portion of the existing general load is counted at 100 % before the 40 % factor applies?
- 12098Which is a condition for using the NEC 2020/2023 multifamily optional method of 220.84?
- 12099An existing 200 A service shows a 1-year maximum demand of 110 A. A 40 A load is added. Using NEC 2020/2023 220.87, what is the resulting calculated load?
- 12101Under NEC 2020/2023 220.60, a dwelling has 10 kW of electric heat and a 5,000 VA AC unit that do not run together. What load is used in the standard method?
- 12102An 8-unit building has 900 ft2 units, each with two small-appliance and one laundry circuit. What is the NEC 2020/2023 standard method demand for these loads?