Question 12082 of 1033 · Washington 01 Journey Level Electrician Exam
Under the NEC 2020 or 2023, what is the feeder load for 25 household electric dryers rated 5,000 W each?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12082
- B: 42,500 VA
Explanation
Each dryer counts at 5,000 VA (220.54): 25 x 5,000 = 125,000 VA. For 24 to 42 dryers the factor is 35 % minus 0.5 % per dryer above 23: 35 - 1 = 34 %. 125,000 VA x 0.34 = 42,500 VA.
More questions: Load Calculations
- 12083Six 12 kW ranges are on one apartment feeder. What range demand load applies under the NEC 2020 or 2023?
- 12084Using NEC 2020/2023 Table 220.55 Column C, what is the demand for twelve 12 kW ranges?
- 12085A 28-unit building has one 12 kW range per unit. What is the range demand load under the NEC 2020 or 2023?
- 12086Under the NEC 2020 or 2023, what is the demand load for one 15 kW household range?
- 12087Under the NEC 2020 or 2023, an 8 kW cooktop and a 4 kW wall oven in the same kitchen are on one branch circuit. What is the branch circuit load?
- 12088Four ranges on one feeder are rated 10, 12, 14 and 18 kW. Using NEC 2020/2023 Table 220.55 Note 2, what is the demand load?