Question 12088 of 1033 · Washington 01 Journey Level Electrician Exam

Four ranges on one feeder are rated 10, 12, 14 and 18 kW. Using NEC 2020/2023 Table 220.55 Note 2, what is the demand load?

Exactly one answer is correct.

Show solution

Correct answer to question 12088

  • D: 18.7 kW

Explanation

Ranges under 12 kW count as 12 kW for averaging: (12 + 12 + 14 + 18) / 4 = 14 kW, which is 2 kW over 12, so and Column C for four ranges (17 kW) rises 10 %: 17 x 1.10 = 18.7 kW.

Next to question ›